PR=NTSB Preliminary Report.
ME=Main Engine.
Technical terms of the diagram see below.
Reading between the lines to fill the gaps of the PR I expect that power was available without any interruption during the whole voyage as there is no mention that any of the DG was shut down though various breakers tripped which caused the blackouts.
As the PR mentions it, during the 1st blackout the supply of the HV BUS (see below) was never interrupted as DG3 and DG4 were still both running normally. In case of voltage or frequency fault the generators would have been automatically disconnected, which did not occur.
Only the LV BUS was affected due to the unexpected disconnection of TR1.
There was always enough electrical power available (unless DG3 and DG4 would have been stopped before DG2 automatically started at the beginning of the 2nd blackout but the PR does not mention anything about when DG3 and DG4 were shut down) but that power could not be routed due to breakers which unexpectedly tripped for reasons not addressed in the PR.
All AC is 60 Hz, HV=High Voltage 6600V, LV=Low Voltage, in the diagram 440 V.
Dead=Not powered (no voltage present); Live=Powered (operating voltage present),
DG1:
Diesel Generator 1, 4400 kW, 6600 V HV.
DG2:
Diesel Generator 2, 4000 kW, 6600 V HV.
DG3:
Diesel Generator 3, 4000 kW, 6600 V HV.
DG4:
Diesel Generator 4, 4400 kW, 6600 V HV.
DGR1:
Diesel Generator 1 Breaker, connects DG1 to the 6600 V HV BUS.
DGR2:
Diesel Generator 2 Breaker, connects DG2 to the 6600 V HV BUS.
DGR3:
Diesel Generator 3 Breaker, connects DG3 to the 6600 V HV BUS.
DGR4:
Diesel Generator 4 Breaker, connects DG4 to the 6600 V HV BUS.
HV BUS:
6600 V High Voltage Bus, supplies the service step-down transformers TR1 and TR2, the BT (Bow Thruster) and, not shown, the 6600/440 V step-down transformers supplying the reefer container sockets.
It is not clear if the ME (Main Engine) lube oil pumps are fed by a separate step-down transformer, I do not expect them to be 6600 V HV motors, I would even rather expect them to be 440 V LV motors supplied by the 440 V LV BUS but that would contradict the PR.
HVR:
High Voltage Bus Tie Breaker, connects the left part of the 6600 V HV BUS to the right part of the 6600 V HV BUS, HVR remained always closed.
HR1:
Transformer 1 High Voltage Breaker: Supplies the 6600 V High Voltage windings of the step.down transformer 1.
TR1:
Transformer 1, large step-down service transformer which converts 6600 V HV (High Voltage) to 440 V LV (Low Voltage). TR1 and TR2 and not used in parallel.
LR1:
Transformer 1 Low Voltage Breaker: Supplies the 440 V LV BUS.
HR2:
Transformer 2 High Voltage Breaker: Supplies the 6600 V High Voltage windings of the step-down transformer 2.
TR2:
Transformer 2, large step-down service transformer which converts 6600 V HV (High Voltage) to 440 V LV (Low Voltage). TR1 and TR2 and not (!) used in parallel.
LR2:
Transformer 2 Low Voltage Breaker: Supplies the LV BUS (440 V).
LVR:
Low Voltage Bus Tie Breaker, connects the left part of the 440 V LV BUS to the right part of the 440 V LV BUS, LVR remained always closed.
EG:
Emergency Generator, small Low Voltage (440 V) diesel generator starting automatically when LV BUS voltage drops below a Min Threshold longer than an Min Delay.
EBUS:
Emergency Bus (440 V), is fed by the LV BUS when LV BUS voltage present, is disconnected from LV BUS and fed by the EG when the EG is running.
LV BUS:
Low Voltage Bus, supplies all 440 V loads excepted those fed by the EBUS and the reefer container sockets, those are fed by several transformer fed by the HV BUS but are not shown in the diagram.
BT:
Bow Thruster, 3000 kW High Voltage (6600 V) motor, breaker shown closed. Closed breaker implies that the power control cabinet of the BT is supplied by the HV BUS but it does not mean that the BT itself is running. No information is provided about possible use of the bowthruster.
- LEAVING PORT
ME (Main Engine): Running (formally not known exactly when started).
DG1: Not running.
DG2: Not running (probably already configured in stand-by for automatic start).
DG3: Running.
DG4: Running.
DGR1: Open.
DGR2: Open.
DGR3: Closed.
DGR4: Closed.
HV BUS: Live.
HVR: Closed.
HR1: Closed.
TR1: Operating.
LR1: Closed.
HR2: Open.
TR2: No operating.
LR2: Open.
LVR: Closed.
LV BUS: Live.
EG: Not running (in standby for automatic start).
EBUS: Live, powered by LV BUS.
Summary:
Everything is normal.
- FIRST BLACKOUT
PR: “about 0125”; StreamTime LIVE: 2024-03-26/01:24:32 EDT
“>” depicts changes since the previous state.
ME (Main Engine): > Shuts down automatically due to loss of auxiliary systems no longer being powered.
DG1: Not running.
DG2: Not running (probably already configured in stand-by for automatic start).
DG3: Running.
DG4: Running.
DGR1: Open.
DGR2: Open.
DGR3: Closed.
DGR4: Closed.
HV BUS: Live.
HVR: Closed.
HR1: > Open.
TR1: > Not operating.
LR1: > Open.
HR2: Open.
TR2: No operating.
LR2: Open.
LVR: Closed.
LV BUS: > Dead.
EG: > Starts automatically.
EBUS: > Dead until powered automatically by EG when emergency power available.
Summary:
The 1st blackout is partial and only affects 440 V LV as the LV BUS lost power after TR1 was disconnected as HR1 (and LR1) tripped. Emergency Generator EG starts automatically and supplies the 440 V EBUS (StreamTime LIVE Video: 2024-03-26/01:25:01 EDT, cannot be seen well).
It is not known if the transformers supplying the reefer container sockets were automatically disconnected.
DG3 and DG4 are still running and powering the 6600 V HV BUS.
The hydraulic steering gear loses power and all 3 previously running hydraulic pumps stop.
Once emergency power is available, hydraulic pump 3 of the steering gear starts and allows rudder control at reduced speed.
- END OF FIRST BLACKOUT
StreamTime LIVE: 2024-03-26/01:25:31 EDT
“>” depicts changes since the previous state.
ME (Main Engine): Not running, unknown if unsuccessful attempts to restart it were made.
DG1: Not running.
DG2: Not running.
DG3: Running.
DG4: Running.
DGR1: Open.
DGR2: Open.
DGR3: Closed.
DGR4: Closed.
HV BUS: Live.
HVR: Closed.
HR1: > Closed.
TR1: > Operating.
LR1: > Closed.
HR2: Open.
TR2: No operating.
LR2: Open.
LVR: Closed.
LV BUS: > Live.
EG: Still running and supplying the EBUS.
EBUS: Powered by the EG.
Summary:
Power is fully restored as the service transformer TR1 (which caused the blackout as it was disconnected) was reconnected by the crew closing manually HR1 and LR2.
Emergency Generator EG is still running.
It is not known if the transformers supplying the reefer container sockets were automatically disconnected if disconnected as the 1st blackout happened, there is no information available.
PR does not mention if the steering gear resumed regular operation with all 3 hydraulic pumps.
- SECOND BLACKOUT
NTSB (calculated): Ca. 01:27:01; StreamTime LIVE: 2024-03-26/01:26:36 EDT
“>” depicts changes since the previous state.
ME (Maine Engine): Not running, unknown if unsuccessful attempts to restart it were made.
DG1: Not running.
DG2: > Starts automatically due to HV BUS power loss.
DG3: (Probably) Running (PR mentions nothing about shut down).
DG4: (Probably) Running (PR mentions nothing about shut down).
DGR1: Open.
DGR2: Open but will closes automatically after the automatic start of DG2 when voltage and frequency stabilized. Low Voltage is not restored automatically as neither TR1 nor TR2 is fed (the PR does not mention that TR1 was disconnected again, probably immediately when the 2nd blackout occurred).
DGR3: > Open.
DGR4: > Open.
HV BUS: > Dead.
HVR: Closed.
HR1: (>) Probaby open (not confirmed as PR does not mention if it was opened).
TR1: Dead.
LR1: (>) Probably open (not confirmed as PR does not mention if it was opened).
HR2: Open.
TR2: No operating.
LR2: Open.
LVR: Closed.
LV BUS: > Dead.
EG: Still running and supplying the EBUS, the PR does not mention if the EBUS remained powered without interruption since after the start of the EG or if it was the EBUS had to be reconnected to the still running EG immediately after the 2nd blackout. Due to the short delay the EBUS probably never switched back to LV BUS suppy and kept supplying the EBUS without interruption.
EBUS: Powered by the EG (see above).
Summary:
A 2nd blackout occurs due to the disconnection of both DG3 and DG4 as DGR3 and DGR4 tripped for unknown reasons.
Emergency Generator EG is still running and supplies the 440 V EBUS.
Nothing is known about the supply of the transformers supplying the reefer container sockets.
The PR does not mention if HR1 and LR1 opened but they probably opened automatically as the HV BUS lost power in order to be ready to restart TR1 or TR2 when the HV BUS is powered again.
DG2 which was already in stand-by starts automatically when the HV BUS goes dead and supplies the HV BUS when DGR2 closes automatically.
DG2 did not start during the 1st blackout as the HV BUS remained powered by the still running DG3 and DG4 as DGR3 and DGR4 remained both closed, which means that during the 1st blackout everything connected to the HV BUS remained supplied without any interruption, only the LV BUS went dead during the 1st blackout.
The 2nd blackout is a total blackout (excepted for the still running EG supplying the EBUS) as both DG3 and DG4 are disconnected.
- End of Second Blackout (NTSB: 01:27:32; StreamTime LIVE: 2024-03-26/01:27:10 EDT)
“>” depicts changes since the previous state.
ME (Main Engine): Not running, unknown if unsuccessful attempts to restart it were made.
DG1: Not running.
DG2: Running
DG3: (Probably) Running (PR mentions nothing about shut down).
DG4: (Probably) Running (PR mentions nothing about shut down).
DGR1: Open.
DGR2: > Closed automatically.
DGR3: Open.
DGR4: Open.
HV BUS: > Powered by DG2.
HVR: Closed.
HR1: Open (not confirmed but PR but at least HR1 or LR1 must have been open as DGR2 closed).
TR1: Dead.
LR1: Open (not confirmed but PR but at least HR1 or LR1 must have been open as DGR2 closed).
HR2: > Closed manually.
TR2: > Operating.
LR2: > Closed manually.
LVR: Closed.
LV BUS: Powered.
EG: Still running and supplying the EBUS, PR does not mention when EG is shut down.
EBUS: Powered by the EG, supply reverted to LV BUS before EG is shut down.
Summary:
The 2nd blackout ends when TR1 (and not TR2 which was previously in use) gets powered when the crew manually closes HR1 and LR1.
Emergency Generator EG is still running and supplies the 440 V EBUS but is not known when it will be shut down.
The PR does not mention when DG3 and DG4 which were initially running are shut down.